from what I know, this is currently not possible. We are working on projects where this will be needed as well. |
Beta Was this translation helpful? Give feedback.
-
No this is not possible. Switches pose a big problem. Since they are derived from a node breaker model, but powerflow can only be calculated for a bus branch model. |
Beta Was this translation helpful? Give feedback.
-
|
@vogt31337 is right, it can not be calculated within the loadflow. However, we are currently working on a mapping of the current after the loadflow. This should be available within some weeks. |
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
-
Hi,
I was wondering if there is an option to avoid the fusing of two buses if they are connected by a closed switch. If the buses get fused there are no current results for the switch in between those buses.
Is there a way of getting load flow results for closed bus-bus switches?
Beta Was this translation helpful? Give feedback.